screen printing => Equipment => Topic started by: CBCB on October 02, 2017, 02:10:05 PM

Title: Hydro Requirements for our 1st Auto. Is a 200A panel enough?
Post by: CBCB on October 02, 2017, 02:10:05 PM
Hey everyone,

Looking at new spaces to lease as we expand the business. I want to automate as soon as possible. Was hoping to get some real world feedback about how much hydro your shop is running on.

Hydro is cheap up here in Canada, so no gas in our equation.

I have done some math based on the equipment we might want to get, and it seems like we would be cutting it close.

The space we're looking at has a 200A single phase panel.

Right now we run our whole manual operation of a 100A panel, and I think it has some decent room to spare. This logic makes me think it gives us 100A to spare - is that enough to put an automatic press, dryer, and compressor on?

From what I'm seeing, a dryer like the HotRoqit XL pulls 100A on single phase. Not leaving a ton of room to get the press/compressor on there.

I have an electrician coming but was curious about what you guys are running. Anyone getting away with 200A 1P and keeping the presses spinning?
Title: Re: Hydro Requirements for our 1st Auto. Is a 200A panel enough?
Post by: T Shirt Farmer on October 02, 2017, 03:14:18 PM
Even if hydro was free I would still buy a gas dryer especially if you are working with tri blends
Title: Re: Hydro Requirements for our 1st Auto. Is a 200A panel enough?
Post by: Inkworks on October 02, 2017, 03:24:14 PM
I agree 100% on going gas dryer, not only is it much cheaper, it's much better. I'm in BC and we noticed a substantial savings over electric.

Get an electrician to look at the specs of the equipment you're looking at running, it's not like you add up all your breakers to find the total. We have 400 amps single phase coming in, but all of our breakers add up to close to 1000amps.
Title: Hydro Requirements for our 1st Auto. Is a 200A panel enough?
Post by: CBCB on October 02, 2017, 03:35:20 PM
I agree 100% on going gas dryer, not only is it much cheaper, it's much better. I'm in BC and we noticed a substantial savings over electric.

Get an electrician to look at the specs of the equipment you're looking at running, it's not like you add up all your breakers to find the total. We have 400 amps single phase coming in, but all of our breakers add up to close to 1000amps.

Our first dryer will be electric for a couple reasons. Hydro is a lot cheaper here in MB than BC. Biggest challenge with gas so far has been finding the right building.
Plan is to go gas when we are looking at feeding two autos down the same conveyor, but for now it’s seeming like a lot less headaches to stay electric.
I don’t think there is a gas dryer even running in this province right now.

What equipment do you have running smoothly on 400a? Two autos or one?


Sent from my iPhone using Tapatalk
Title: Re: Hydro Requirements for our 1st Auto. Is a 200A panel enough?
Post by: Croft on October 02, 2017, 04:14:29 PM
I ran an air 6 colour sportsman , 2 x 220 volt spot dryers 17 amp each , a 5 horse compressor 20 amp and Radicure 4 panel dryer running around 90 amps on, plus light table computer etc . It was maxed out and never really felt comfortable.

I'm pretty sure if you got a servo driven press you would be short on power.
Title: Re: Hydro Requirements for our 1st Auto. Is a 200A panel enough?
Post by: inkman996 on October 02, 2017, 04:18:06 PM
I tell you we run on a 200A 3 phase service and it amazes me how much we have on it. I know most things do not run at the AMPs on the nameplate once up and running but still. Currently we run


Electric Dryer 80A
2 Quartz Flash 75A
3 Emb machines Note surte the amps
Compressor 35A
8 Color Auto servo AC not sure the amps
220 Volt Heat Press
MSP3140 Exposure Unit
And everything else such as printers lights, pumps computers etc.

Never blow the main breaker thanks god.

We did once have our electrician balance the panel out he said it was a hot mess  but has it laid out well with room for a couple more breakers.
Title: Re: Hydro Requirements for our 1st Auto. Is a 200A panel enough?
Post by: CBCB on October 02, 2017, 08:41:59 PM
Thanks! That's a ton of stuff on 200a 3p.

I'll know soon what kind of upgrades are possible. We'll at least be able to get our manual setup in there on 200A, but the biggest reason for moving is to get the auto in there. Hoping I can get the first auto going without a big hydro upgrade.
Title: Re: Hydro Requirements for our 1st Auto. Is a 200A panel enough?
Post by: jsheridan on October 02, 2017, 11:17:51 PM
 There is a big difference in a 200 amp 3 phase commercial panel versus a 200 amp household 230 panel.

You're going to need 3phase to run the auto and the flashes.
Title: Re: Hydro Requirements for our 1st Auto. Is a 200A panel enough?
Post by: islandtees on October 02, 2017, 11:24:25 PM
Minimum 200amp 3 phase. You will regret later you didn't get at least that.
Title: Re: Hydro Requirements for our 1st Auto. Is a 200A panel enough?
Post by: CBCB on October 03, 2017, 08:05:10 AM
You're going to need 3phase to run the auto and the flashes.

This is where I get confused with people’s advice.
If all the equipment is single phase, why would I ‘need’ 3-phase?

Couple comments up is someone with 400a 1p.



Sent from my iPhone using Tapatalk
Title: Re: Hydro Requirements for our 1st Auto. Is a 200A panel enough?
Post by: mimosatexas on October 03, 2017, 10:05:28 AM
Without 3 phase arent you basically going to need a phase converter for certain equipment, and aren't you going to spend a bunch more on electric?
Title: Re: Hydro Requirements for our 1st Auto. Is a 200A panel enough?
Post by: islandtees on October 03, 2017, 11:50:57 AM
Most flash units run 3 phase. 40 amps per unit most of the time. Single phase flash at 75 amps times 2 will eat up a lot of the 200 amp single phase panel.
We installed 400 amp 3 phase to be sure we can carry any load.
Title: Re: Hydro Requirements for our 1st Auto. Is a 200A panel enough?
Post by: inkman996 on October 03, 2017, 12:45:49 PM
Most flash units run 3 phase. 40 amps per unit most of the time. Single phase flash at 75 amps times 2 will eat up a lot of the 200 amp single phase panel.
We installed 400 amp 3 phase to be sure we can carry any load.

Our two are rated 75A on the plate 3 phase but I know they run a lot lower than that when warmed up.
Title: Re: Hydro Requirements for our 1st Auto. Is a 200A panel enough?
Post by: Sbrem on October 03, 2017, 06:01:48 PM
for what it's worth, here we run a Gauntlet S, MHM Synchroprint, with a Calmat and an MSI flash unit, and 2 Advance TexAir Electric/Gas dryers, a 48" and a 60", and a third small electric dryer, MH lamp, screen dryer, and that's pretty much it, on a 300 amp 3 phase service. Computers and phones and the like are on the landlord's bill, which I'm sure is considered in our rent.

Steve
Title: Re: Hydro Requirements for our 1st Auto. Is a 200A panel enough?
Post by: jsheridan on October 03, 2017, 06:43:56 PM
You're going to need 3phase to run the auto and the flashes.

This is where I get confused with people’s advice.
If all the equipment is single phase, why would I ‘need’ 3-phase?

Couple comments up is someone with 400a 1p.


Sent from my iPhone using Tapatalk

I can see the confusion.

A 200a 3 phase panel is close to the same as 400a single panel. The major difference will be the cost to operate the single panel, is double that of the 3 phase, and why we recommend using 3phase, it's a cost issue mostly.



 
Title: Re: Hydro Requirements for our 1st Auto. Is a 200A panel enough?
Post by: Gilligan on October 03, 2017, 07:37:39 PM
I run a 6 color Sabre, 3 panel Radicure, HAD a 3140, 1,600 sqft air conditioned (poorly, so it ran steady), heat press, 2 embroidery machines, several computers, all the bells and whistles needed to run a shop.

I don't have a main breaker but the wires are rated for 100 Amps (3 phase).  I've put a clamp meter on it and we are JUST clipping that 100 amps.

If I had 200 Amps, I'd be dropping in a 2nd air conditioner no doubt!!!  That's one motivation for taking the additional 800 sqft when my tenants up front move out.  Can take over their electrical box to add more juice!
Title: Re: Hydro Requirements for our 1st Auto. Is a 200A panel enough?
Post by: Inkworks on October 03, 2017, 09:26:16 PM
[

What equipment do you have running smoothly on 400a? Two autos or one?



Major equipment off the top of my head:
12/14 all electric/servo Challenger Falcon
18" x 22" Quartz Flash
18" x 28" Quartz Flash
(both converted from 3ph. to single phase, easily, with almost zero parts needed, after being repeatedly told it wasn't possible, like there are 3ph lightbulbs or something... running for many years now with no problems)
M&R Heatwave dryer (primarily gas, but a big electric blower)
7.5hp 30cfm@100psi compressor
24" x 14' Hix all electric conveyor dryer
2 pad printers (primarily pneumatic)
2 hix heat presses
8000 watt exposure light and 6' x 4' vacuum frame
3000 watt nuarc fliptop exp. unit
Stihl pressure washer
vinyl cutter
Central Air along with large 2-piece aux. unit.
2 portable swamp coolers
Table saw
Drill press
bench grinder etc.
3000 sq.ft. of fluorescent lighting, computers, fridge, microwave, coffee maker and all the other normal stuff plugged into all the outlets.
Title: Re: Hydro Requirements for our 1st Auto. Is a 200A panel enough?
Post by: CBCB on October 29, 2017, 05:02:16 PM
Got a space with 5000sq/ft and 200A 3-phase service., with room to upgrade in the future if need be. Auto time!